On May 6, 3:29*am, wrote:
In alt.engineering.electrical Don Kelly wrote:

| Now - is this all germane to household protection? You say not and I agree
| with you- because household equipment can ride through - at worst- doubling
| of the clamped voltage for a very short time even though the clamped voltage
| is relatively small compared to the peak of the incoming surge. --

What if the surge is an extreme case (e.g. direct strike very near) and it is
arriving at protection devices in common mode (same polarity on all three
wires). *Bud's assertion _seems_ to be that no surge could ever be of the
type with substantial energy at high frequencies. *My belief is that they
can, and will at times. *Lightning strokes have that energy, or else you
would not receive them on UHF. *If the stroke is strong _and_ close (e.g..
less line inductance between the point of strike and where it is being
considered), then more of that UHF energy will arrive.

I have seen damage patterns in electronics that strongly suggests that there
were specific paths involved based on minor levels of reactance in the circuit.
A resistor would be melted along one path, but not so along another which had
a small inductor (3 turns in air) in the way. *And this device (a VCR) was on
a surge protector along with a TV that was unharmed.

If Bud is just arguing about the _typical_ (median?) surge level, then maybe
we are arguing apples and oranges. *I certainly don't intent to protect against
50% of surges. *My target is better than 99%. *I want to feel comfortable
sleeping through a severe thunderstorm while my computers and media center
remain plugged in.

I do agree that things can survive at the clamping voltage. *But there has to
be a clamping situation. *It's too easy for a surge to come in as a common
mode surge where the voltage difference across the MOVs would be (nearly) zero.
Then all we have is a propogating wavefront. *And if it is strong and/or close
then we have very fast rise times. *And it passes by the MOVs "laterally".

There's probably a big difference of opinion about just how much protection is
worth it. *But one thing I do see in at least part of this thread is that Bud
focuses on quoting things other people say, and does very little to express
things in his own words. *That suggests he reads but does not fully understand.
And that means I can't ask questions of what is said in the thread. *Since Bud
can't (or won't) defend what he's saying in his own words based on his own
knowledge, it's not really a two way street. *His "experts" are not involved
in the debate; they can neither defend their position nor be questioned about
it to get more details.



I find Bud's use of actual references interesting and think they add
to his credibility. Trying to suggest that someone using references
such as the IEEE to support their position detracts from their
credibility is preposterous. And trying to impugn him in this fashion
only detracts from your credibility.





It also has brought some other comments from people who are either anti-social
insulting types, or those that just don't understand what is said (apparently
having never dealt with transmission line propogation), or both. *But at least
I know who not to trust any technical opinions from when I have question to
ask about things I want to learn more about.

--
|WARNING: Due to extreme spam, I no longer see any articles originating from *|
| * * * * Google Groups. If you want your postings to be seen by more readers |
| * * * * you will need to find a different place to post on Usenet. * * * * *|
| Phil Howard KA9WGN (email for humans: first name in lower case at ipal.net) |


  #202  
Old May 7th 08, 04:28 PM posted to alt.comp.hardware.pc-homebuilt,alt.home.repair,alt.engineering.electrical,alt.tv.tech.hdtv,sci.electronics.basics
Bud--
external usenet poster
 
Posts: 102
Default Surge / Ground / Lightning

Mike Tomlinson wrote:
In article , bud--
writes

Last I heard UK phone entry protectors did not clamp the voltage to
earth.


You're quite correct. It's a practice that the GPO (forerunner to
British Telecom) abandoned in the 1960s, showing how up to date w_'s
"knowledge" is.


Phone wires were clamped to ground before the 1960s?

--
bud--
  #203  
Old May 7th 08, 04:49 PM posted to alt.comp.hardware.pc-homebuilt,alt.home.repair,alt.engineering.electrical,alt.tv.tech.hdtv,sci.electronics.basics
Bud--
external usenet poster
 
Posts: 102
Default Surge / Ground / Lightning

VWWall wrote:
wrote:

"New thermally enhanced MOVs help protect a wide variety of low-power
systems against damage caused by over-current, over-temperature and
over-voltage faults, including lightning strikes, electrostatic
discharge (ESD) surges, loss of neutral, incorrect input voltage and
power induction.


I had a microwave oven that had a MOV across the 120V line ahead of the
power switch. The other side of the 120/240 20A circuit supplied a
refrigerator. The loss of the neutral applied a good part of the 240V
across the MOV when the refrigerator attempted to start.

The MOV didn't last long! It would probably have been OK on the load
side of the switch.


Using a MOV to protect against loss of neutral (in the article) is
rather futile. Sustained overvoltage will rapidly kill them. Although if
the protected load was across the MOV and a fuse was ahead of both
protection may work. Would be interesting why the MOV was ahead of the
switch.


I know that refrigerators should be alone on a "home run" circuit, and
neutrals shouldn't be connected with wire nuts, but that wasn't how it was!

My only complaint with some plug-in protectors is that the MOVs are
often much too small. I've also seen some with only a line-line MOV.


I would only buy one with fairly high ratings (which are readily
available).

UL, as far as I know, requires MOVs to be L-N, L-G, N-G. I thought that
was the standard since the start, which w_ said was 1985.

--
bud--


  #204  
Old May 7th 08, 05:04 PM posted to alt.comp.hardware.pc-homebuilt,alt.home.repair,alt.engineering.electrical,alt.tv.tech.hdtv,sci.electronics.basics
charles
external usenet poster
 
Posts: 3,383
Default Surge / Ground / Lightning

In article ,
bud-- wrote:
Mike Tomlinson wrote:
In article , bud--
writes

Last I heard UK phone entry protectors did not clamp the voltage to
earth.


You're quite correct. It's a practice that the GPO (forerunner to
British Telecom) abandoned in the 1960s, showing how up to date w_'s
"knowledge" is.


Phone wires were clamped to ground before the 1960s?


not as such, but phones in rural areas often had an earth terminal on the
household terminal box.

--
From KT24 - in "Leafy Surrey"

Using a RISC OS computer running v5.11

  #205  
Old May 7th 08, 05:30 PM posted to alt.comp.hardware.pc-homebuilt,alt.home.repair,alt.engineering.electrical,alt.tv.tech.hdtv,sci.electronics.basics
Bud--
external usenet poster
 
Posts: 102
Default Surge / Ground / Lightning

wrote:
In alt.engineering.electrical bud-- wrote:
|
wrote:
| In alt.engineering.electrical bud-- wrote:
| |
wrote:
| | In alt.tv.tech.hdtv bud-- wrote:
|
| | | w_' professional engineer source says 8 micoseconds with most of the
| | | spectrum under 100kHz.
| |
| | Even with 1 nanosecond rise time, most of the energy will be present in
| | the spectrum below 100 kHz. That means nothing when the surge is strong
| | enough to have energy above some frequency that is relevant to the whole
| | system involved that can do damage. That frequency might be 100 Mhz for
| | some thing, and 1 GHz for other things.
| |
| | Still missing - your source. Nanosecond risetime. 100MHz spectrum.
|
| Observation. Of course this is a concept you cannot understand.
|
| Observation proves flying saucers and magic.
|
| Without supporting sources it is Phil's Phantasy Physics.
| Where is a source that supports your belief in nanosecond risetimes and
| 100MHz spectrum?

There is no point in spending the effort to find some quotable source because
you wouldn't know what to do with it.


In other words - it is Phil’s Phantasy Physics, so no supporting link
exists.

--
bud--
  #206  
Old May 7th 08, 05:34 PM posted to alt.comp.hardware.pc-homebuilt,alt.home.repair,alt.engineering.electrical,alt.tv.tech.hdtv,sci.electronics.basics
Bud--
external usenet poster
 
Posts: 102
Default Surge / Ground / Lightning

wrote:
On May 5, 2:20 pm, wrote:
In alt.engineering.electrical wrote:

| On May 5, 1:44?am, wrote:
| In alt.tv.tech.hdtv bud-- wrote:| wrote:
|
| | In alt.engineering.electrical Leonard Caillouet wrote:| | wrote in message
|
| | ...
| | | In alt.tv.tech.hdtv Franc Zabkar wrote:
| | |
| | |
| | | The MOVs will act like conductors when they are clamping. ?The surge will
| | | take both paths ... the path through the MOVs, and the path going past the
| | | MOVs. ?In general, about 50% will go each way. ?That can vary at higher
| | | frequencies.
| | |
| | | Why would you assume that 50% will go each way when you don't know the
| | | impedance of each direction? ?When conducting, or at failure, the MOV has a
| | | very low impedance.
| |
| | There is a distinction between "go each way" and "what comes back" due to
| | the impedance. ?It will be about 50% that goes each way _because_ the power
| | itself does not (yet) know the impedance (at a distance), until it gets
| | there.
| |
| | Another installment of Phil's Phantasy Physics using transmission line
| | theory.
|
| Not understanding it is your loss.
|
|
| I have to agree that this is Phantasy Physics. We're supposed to
| believe that a surge reaching a MOV is going to split 50-50, with half
| of it going to the MOV path and half moving on down the line,
| reagrdless of the impedance of the two paths? That would render all
| surge protection about 50% effective.

You did not read very carefully. The reference to 50-50 split is about the
contribution of the MOVs themselves. That is an essential understanding of
the components so the whole system can be figured out. The impedance down
the paths is another separate component, which also has to be figured in
when determining the whole picture.

You have confused a component with the entire system. You need to read more
carefully. Or you need to understand the distinction of individual components
as they apply to the whole system

The whole wiring system is extrememly complex. It cannot be understood
properly without first understanding the components. And that includes
understanding that MOVs, when they conduct, do look to the propogating
energy as two paths to go down, and it will (initially) go both ways in
about an equal amount.


Maybe you should review what you actually stated in the context of
current surge supression discussion:
"
"The MOVs will act like conductors when they are clamping. The surge
will
| | take both paths ... the path through the MOVs, and the path
going past the
| | MOVs. In general, about 50% will go each way. That can vary at
higher
| | frequencies. "

That sure sounds like 50% of the surge is going through the MOV and
the other 50% is going on past it to the protected equipment.

And that I would have to agree with Bud on, it's phantasy physics,
because if it were true, no type of surge protection would work,
because it would only be 50% effective.


He is using transmission line effects which Martzloff investigated and
said do not come into play unless the circuit is 200m long. Phil claims
high frequencies.

Still missing - a source that supports nanosecond risetimes and 100MHz
spectrum.

--
bud--
  #207  
Old May 7th 08, 05:42 PM posted to alt.comp.hardware.pc-homebuilt,alt.home.repair,alt.engineering.electrical,alt.tv.tech.hdtv,sci.electronics.basics
Bud--
external usenet poster
 
Posts: 102
Default Surge / Ground / Lightning

w_tom wrote:
On May 6, 1:00 pm, bud-- wrote:


w_ can't understand his own hanford link. It is about "some older
model" power strips and says overheating was fixed with a revision to
UL1449 that required thermal disconnects. That was 1998.


Bud will only challenge the hanford link because he cannot challenge
those 'scary pictures'.


w_ only provides those ‘scary pictures’ because he has no valid
technical arguments.

Still missing - a link to any source that says UL listed plug-in
suppressors made after 1998 are a problem.

Another is a fire marshal describing
why plug-in protectors can create house fires.


The fire marshal said: "More modern surge suppressors are manufactured
with a Thermal Cut Out mounted near, or in contact with, the MOV that is
intended shut the unit down overheating occurs.[sic]"


And then Bud posts a half fact. UL1449 was created on 28 Aug 1985 -
not in 1998 as Bud claims.


It is really hard to understand how someone could be stupid enough to
not know the difference between a creation date and a revision date.

From w_'s hanford link:
"Underwriters Laboratories Standard UL 1449, 2nd Edition, Standard For
Safety For Transient Voltage Surge Suppressors, now requires thermal
protection in power strips. This protection is provided by a thermal
fuse located next to the MOV."

The fire marshal says the same thing (above)

If w_ had any knowledge of the field he would know UL 1449, 2nd Ed was
effective in 1998.

Bud refuses to post a
specification for one simple reason.


Posted often and ignored. Another of w_'s favorite lies.

In reply, this is
what Bud is really promoting - these 'scary pictures':
http://www.hanford.gov/rl/?page=556&parent=554


The lie repeated. But w_ is a fan of Josef Goebbels and thinks if you
repeat a lie often enough, people will believe it.


Still missing - a link to another lunatic that says plug-in suppressors
are NOT effective.

Still missing – answers to embarrassing questions:
- Why do the only 2 examples of surge suppression in the IEEE guide use
plug-in suppressors?
- Why does the NIST guide says plug-in suppressors are "the easiest
solution"?
- Why do all but one of w's "responsible manufacturers" make plug-in
suppressors?
- Why does SquareD say in addition to their "whole house" suppressors
"electronic equipment may need additional protection" from plug-in
suppressors.
- Why aren't airplanes crashing daily when they get hit by lightning (or
do they drag an earthing chain)?

–-
bud--
  #208  
Old May 7th 08, 05:47 PM posted to alt.comp.hardware.pc-homebuilt,alt.home.repair,alt.engineering.electrical,alt.tv.tech.hdtv,sci.electronics.basics
Bud--
external usenet poster
 
Posts: 102
Default Surge / Ground / Lightning

wrote:
In alt.engineering.electrical bud-- wrote:
|
wrote:
| In alt.engineering.electrical Don Kelly wrote:
|
| | Now - is this all germane to household protection? You say not and I agree
| | with you- because household equipment can ride through - at worst- doubling
| | of the clamped voltage for a very short time even though the clamped voltage
| | is relatively small compared to the peak of the incoming surge. --
|
| My belief is that they
| can, and will at times.
|
| People believe in flying saucers.
| Where is a source that supports your belief?

My observations support my belief.


Observations support belief in astrology, reflexology, homeopathy,
dowsing, healing touch, Feng Shui, Sylvia Brown, ....


| I do agree that things can survive at the clamping voltage. But there has to
| be a clamping situation. It's too easy for a surge to come in as a common
| mode surge where the voltage difference across the MOVs would be (nearly) zero.
| Then all we have is a propogating wavefront. And if it is strong and/or close
| then we have very fast rise times. And it passes by the MOVs "laterally".
|
| Where is a source that supports your belief in nanosecond risetimes and
| 100MHz spectrum?

Another poster followed up to my post you just followed up to that also has
experienced the same thing.


I am not interested in direct lightning strikes to my house. Protection
requires lightning rods.

I am interested in surge protection. That is surges coming in on utility
wires, direct induction, ground potential rise, ....

Martzloff says transmission line effects require 200m branch circuits.

You disagree with Martzloff (and have said "he flubbed the experiment")
but provide no sources that agree with your belief.


| But one thing I do see in at least part of this thread is that Bud
| focuses on quoting things other people say, and does very little to express
| things in his own words.
|
| I focus on the real world. You focus on your beliefs.

You focus on citing and quoting things you do not understand well enough to
just talking about them in technical terms.


In other words, it is Phil’s Phantasy Physics.

Where is a source that supports your belief in nanosecond risetimes and
100MHz spectrum?
There should be plenty of sources.

--
bud--
  #209  
Old May 7th 08, 06:31 PM posted to alt.comp.hardware.pc-homebuilt,alt.home.repair,alt.engineering.electrical,alt.tv.tech.hdtv,sci.electronics.basics
VWWall
external usenet poster
 
Posts: 8
Default Surge / Ground / Lightning

bud-- wrote:
VWWall wrote:
wrote:

"New thermally enhanced MOVs help protect a wide variety of low-power
systems against damage caused by over-current, over-temperature and
over-voltage faults, including lightning strikes, electrostatic
discharge (ESD) surges, loss of neutral, incorrect input voltage and
power induction.


I had a microwave oven that had a MOV across the 120V line ahead of
the power switch. The other side of the 120/240 20A circuit supplied
a refrigerator. The loss of the neutral applied a good part of the
240V across the MOV when the refrigerator attempted to start.

The MOV didn't last long! It would probably have been OK on the load
side of the switch.


Using a MOV to protect against loss of neutral (in the article) is
rather futile. Sustained overvoltage will rapidly kill them. Although if
the protected load was across the MOV and a fuse was ahead of both
protection may work. Would be interesting why the MOV was ahead of the
switch.


Good question. In the MW oven case, the switch was a relay controlled
by the timer circuit. It was probably easier to locate the MOV at the
line input.

I have seen cases with a "blown" MOV and the circuit protector tripped.
The MOV, if it tripped the protector, may have saved the following
circuits from the over-voltage condition for a longer period of time. I
haven't tried to calculate the conditions under which this would work.

I know that refrigerators should be alone on a "home run" circuit, and
neutrals shouldn't be connected with wire nuts, but that wasn't how it
was!

My only complaint with some plug-in protectors is that the MOVs are
often much too small. I've also seen some with only a line-line MOV.


As you know, MOVs lose their capacity each time a "spike" causes them to
conduct. This reduces the remaining capability to handle "surges".

I would only buy one with fairly high ratings (which are readily
available).


True, but some are marketed as "surge protected" with minimal capacity.
I've replaced the MOVs in several cheap multiple socket strips with
higher rated MOVs from Radio Shack.

UL, as far as I know, requires MOVs to be L-N, L-G, N-G. I thought that
was the standard since the start, which w_ said was 1985.


I think the UL requires only that the MOVs don't start a fire when
exposed to conditions which cause their break-down. They don't rate
their ability to function as "surge protectors".

--
Virg Wall, P.E.
  #210  
Old May 7th 08, 08:17 PM posted to alt.comp.hardware.pc-homebuilt,alt.home.repair,alt.engineering.electrical,alt.tv.tech.hdtv,sci.electronics.basics
[email protected]
external usenet poster
 
Posts: 30
Default Surge / Ground / Lightning

I think the UL requires only that the MOVs don't start a fire when
exposed to conditions which cause their break-down. *They don't rate
their ability to function as "surge protectors".



UL evaluates surge suppressors for fire, electric shock and personal
injury hazards, and also measures and categorizes the devices for how
much voltage they can "clamp," thus preventing excess voltage from
passing through to electronic equipment. UL refers to this as a
"suppressed voltage rating," with ranges from 330V (volts) to 4000V.
Believe it or not, the lower the rating, the better the protection.

Whatever surge suppression protection you're looking for, make sure
the surge suppressor has been tested and Listed to the stringent
requirements of UL 1449, the Standard for Transient Voltage Surge
Suppressors.

http://www.ul.com/consumers/surge.html

http://ulstandardsinfonet.ul.com/toc...=s&fn=1449.toc
 




Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
inverto idl-7000 pvr - lightning [email protected] UK digital tv 1 July 24th 06 05:40 PM
lightning hit my Sal UK digital tv 28 February 28th 05 03:48 PM
help! Lightning has striken my system Michael Best Satellite tvro 11 September 7th 03 10:40 PM
Lightning and aerials - LONG POST Duncan Ross UK digital tv 13 July 27th 03 04:27 PM
Rigger's diary - lightning Duncan Ross UK digital tv 13 July 22nd 03 03:06 AM


All times are GMT +1. The time now is 08:14 PM.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2021, Jelsoft Enterprises Ltd.
Copyright ©2004-2021 HomeCinemaBanter.
The comments are property of their posters.