In uk.tech.broadcast, on Sun, 1 Jun 2008 17:23:10, Zathras wrote:
My broadcasting experience is that we'd have had fewer bits of broken kit and fewer outages if we hadn't had any UPSs at all! Agreed! At out new building, we don't have any - just two kinetic batteries and a generator that comes up before the KB's spin down. Outstanding idea. -- Jim Crowther |
Catastophic failure on ITV
"Zathras" wrote in message ... snip At out new building, we don't have any - just two kinetic batteries and a generator that comes up before the KB's spin down. I assume by "kinetic batteries" you mean 'motor-flywheel-generators', if so, how is this implemented? |
Catastophic failure on ITV
On Sun, 01 Jun 2008 17:23:10 +0100, Zathras wrote:
At out new building, we don't have any - just two kinetic batteries and a generator that comes up before the KB's spin down. Hopefully the generator comes up before the kinetics spin down... -- Cheers Dave. |
Catastophic failure on ITV
Java Jive wrote:
Somehow, I can't show any surprise ... snips long scary story Our critical servers are all fitted with dual PSUs. The idea is that one is fed from the UPS, and one straight from the mains. Lose the mains, and the UPS kicks in. Lose the UPS, and they run straight from the mains. (we're moving machine rooms soon, and as I now "own" some of the servers, I'll check that they really are like that in their new home) Repeat after me: "No Single Point Of Failure" :) Andy |
Catastophic failure on ITV
On 01/06/2008 23:02, Andy Champ wrote:
Our critical servers are all fitted with dual PSUs. The idea is that one is fed from the UPS, and one straight from the mains. Lose the mains, and the UPS kicks in. Lose the UPS, and they run straight from the mains. Early morning generator test occurs, you loose mains for a few seconds, no problem UPS cuts in, generator starts, that extra server you added recently increases the inrush current as half of your PSUs come back on line at once, mains MCB trips, current drawn by the other half of your PSUs is double normal, workload increases on the servers as people start logging on for the day, servers draw that critical few extra amps, a circuit breaker on the UPS reaches its limit and it trips, it goes dark and quiet ... |
Catastophic failure on ITV
On Sun, 01 Jun 2008 23:21:28 +0100, Andy Burns wrote:
Early morning generator test occurs, you loose mains for a few seconds, no problem UPS cuts in, generator starts, that extra server you added recently increases the inrush current as half of your PSUs come back on line at once, mains MCB trips, AWOOGA, AWOOGA, blooming great alarm goes off triggered by detecting voltage across the MCB(s)... -- Cheers Dave. |
Catastophic failure on ITV
"Richard Tobin" wrote in message ... In article , :Jerry: wrote: It seems from the DS posting made today, that the UPS let out a nice fat spike. There is some what of an irony in that, of all the devices to *cause* an outage?! :~( In 30 years of using computers, I have experienced innumerable computer outages because of UPSes being installed, removed, serviced, or exploding, and have never once had my computer stay up, or even shut down in an orderly manner, when the mains was cut. Heading up to the millenium I was responsible for maintaining a large test facility and we were pulled in 4 weekends in a row to test the power backup facilities. First weekend, after the power had been cut, the electricians discovered that no one had thought to put diesel in the generator. Second weekend the UPS went bang. Third weekend it was discovered that my test facility was not actually connected into the power backup network. Fourth weekend, power stayed up, but half the equipment went down because of spikes on the voltage at switching. The fifth weekend was the millenium itself, thankfully power backup was never needed. //Clive. |
Catastophic failure on ITV
In article id, Jim
Crowther scribeth thus In uk.tech.broadcast, on Sun, 1 Jun 2008 17:23:10, Zathras wrote: My broadcasting experience is that we'd have had fewer bits of broken kit and fewer outages if we hadn't had any UPSs at all! Agreed! At out new building, we don't have any - just two kinetic batteries and a generator that comes up before the KB's spin down. Outstanding idea. Yep UPS's aren't the most reliable backup power. We directly float quite a bit of Telecoms equipment off battery banks at either 24 or 48 volts, Much more reliable that whopping it back up to 230 volts;)).. -- Tony Sayer |
Catastophic failure on ITV
On Sun, 01 Jun 2008 22:01:21 +0100 (BST), "Dave Liquorice"
wrote: On Sun, 01 Jun 2008 17:23:10 +0100, Zathras wrote: At out new building, we don't have any - just two kinetic batteries and a generator that comes up before the KB's spin down. Hopefully the generator comes up before the kinetics spin down... It's regularly run, tested and maintained - if it's like our last one, probably a twin engine unit. Totally reliable IME. -- Z |
Catastophic failure on ITV
On Sun, 1 Jun 2008 20:59:13 +0100, ":Jerry:"
wrote: "Zathras" wrote in message .. . snip At out new building, we don't have any - just two kinetic batteries and a generator that comes up before the KB's spin down. I assume by "kinetic batteries" you mean 'motor-flywheel-generators', if so, how is this implemented? Two contra-rotating units (fearlessly) located on the roof. They supply energy instantly and for a longer time than the generator takes to start and stabilise. I don't have any more detail of our installation so for more than that, Google is the place to look - KBs are amazing devices! -- Z |