do I need a surge protector?
On Feb 24, 10:52 pm, "w_tom" wrote:
Let's return to Jane's TV. Assume your 330 volts protector is adjacent. A surge comes down all AC wires seeking earth ground. Your protector may or may conduct surge current from one wire to others. Will that surge seek earth ground down a safety ground wire that is now charged at something less than 12,000 volts? Not when surge has a better path to earth, destructively, through Jane's TV and coax cable. All interconnected equipment needs to be connected to the same plug-in suppressor, or interconnecting wires need to go through the suppressor. Other external wires like cable TV, phone, ... also need to go thorough the suppressor. The voltage on ALL wires (power and signal) to protected devices is clamped to the common ground at the suppressor. Multiport suppressors are described in the IEEE guide at: http://www.mikeholt.com/files/PDF/Li...ion_May051.pdf And the NIST guide at: http://www.nist.gov/public_affairs/p.../surgesfnl.pdf A plug-in protector too far from earth ground and too close to TV does not even claim to provide protection. Complete nonsense. Worse, that plug-in protector costs $25 or $125 per protected appliance. Which is why you don't buy one for your alarm clock. But a HDTV system is high value. -- bud-- |
do I need a surge protector?
"R Sweeney" wrote in message . .. "Jane" wrote in message ups.com... Just bought a Samsung 46" HDTV at Circuit City. They tried to talk me into a very expensive surge protector. They also said I MUST have a Monster HDMI cable for $125 which I later found out was bull. So I decided to wait on their surge protector and ask you guys out there for advice. Do I need it? What brand is best? I have a really good one for my computer but it's paid for by my company. I also have a Liebert which costs about $30 but I believe is meant mostly for computers, or are they generic? No one needs ANYTHING made by Monster. They might as well change the name of the company to Fraud Inc. However, a quality surge protector is a wise investment for home theater. There are many on the market, even the best are less than $50. The Joule rating is the amount of energy the surge arrestor can swallow without blowing up - higher is better. Your Liebert is better than fine. Joule ratings are not necessarily reliable indicators for comparison. Let through voltage and current peak ratings are other ratings that should be considered. BTW, w_tom stated that most units start to clamp at 330volts, but actually, the better units these days have a max let through voltage of 330 volts. As for Joule ratings, yes, more is better, but understand that the ratings can be misleading. For instance, the two units that I recommended earlier, the CyberPower 1090 and the Panamax have almost identical complements of MOVs, yet the CP has a joule rating of more than twice the Panamax. They obviously are counting the capacity of all of the MOVs. This is misleading because it is impossible for all of them to be operating at the same time, as they are protecting the three combinations of H-N, H-G, and N-G. You simply cannot clamp on all those combinations at the same time. Read and compare all of the specs carefully, and be wary of those that are missing. Most units give little or no detail, particuarly on the signal line suppression. Some of the Monster products can be found at prices that, while not the cheapest, are competitive with other quality brands. I don't suggest that they are a good value in most cases, but they are a quality product in almost all cases. Filtering claims of improved performance are as bogus as any, but then even reputable SS companies such as Panamax have jumped on that marketing bandwagon. Leonard -------------------------------------------------------------------------------- I am using the free version of SPAMfighter for private users. It has removed 800 spam emails to date. Paying users do not have this message in their emails. Try SPAMfighter for free now! |
do I need a surge protector?
Thanks everyone
I just ordered a Belkin PureAV Isolator. 4720 Joules. My company uses Belkin Isolators for their equipment so I'm hoping they are fairly reliable. Again, thanks. |
do I need a surge protector?
"Jane" wrote Advice would be appreciated. I have learned from a couple of years on this NG and the AVS Forum to pay attention to what Leonard says on matters like this. Unlike some others he values facts and not self image. |
do I need a surge protector?
"Dave Gower" wrote in message ... "Jane" wrote Advice would be appreciated. I have learned from a couple of years on this NG and the AVS Forum to pay attention to what Leonard says on matters like this. Unlike some others he values facts and not self image. Thank you Dave. I do try to do my homework and throw in my version of common sense. I have also learned quite a bit from others, like yourself on these forums. It certainly goes both ways. Leonard -------------------------------------------------------------------------------- I am using the free version of SPAMfighter for private users. It has removed 844 spam emails to date. Paying users do not have this message in their emails. Try SPAMfighter for free now! |
do I need a surge protector?
"Dave Gower" wrote in message
... "Jane" wrote Advice would be appreciated. I have learned from a couple of years on this NG and the AVS Forum to pay attention to what Leonard says on matters like this. Unlike some others he values facts and not self image. I agree with this. Leonard's usually very knowledgable and reliable in his remarks about the deeper tech/electronic stuff. |
do I need a surge protector?
On Feb 25, 3:19 am, "bud--" wrote:
All interconnected equipment needs to be connected to the same plug-in suppressor, or interconnecting wires need to go through the suppressor. That is the point of Bud's papers. They move onward to describe how plug-in protectors also cause damage. A TV is at 8000 volts because a plug-in protector - without proper earthing - contributes to TV damage. Why? TV in another room was not connected through the same protector. What happens to "connected to the same plug-in suppressor" electronics when a kid attaches his Xbox to the TV? Protection is completely compromised - as Bud's own citations note when discussing 'six ports'. Bud forgets to mention that part. Described in technical terms is how damage happened; such as when a kid attaches an Xbox to a TV. Meanwhile, when one 'whole house' protector provides 'properly earthed' protection, then everything is "connected to the same" protector. Bud also forgets to mention his citations also say that. Just another reason why plug-in protectors are recommended by Bud's authors AND why that TV is destroyed by 8000 volts thanks to a plug-in protector. In one post, Bud recommends earthing so that 8000 volts does not damage a TV. In another, Bud claims "surge reference equalizer" does not require earthing. Which is it? Confusion to promote plug-in protectors is his objective. As long as you don't learn facts and numbers, then many will buy what is simplest - a magical plug-in device that violates how effective protection was installed even 50 years ago. He hopes you will not notice this. No plug-in protectors manufacture claims to provide such protection in their numerical specifications. If they did, then they could be sued. Why does Bud intentionally distort what even the IEEE recommends in standards? Remember IEEE does not recommend in papers. IEEE recommends in standards. And IEEE standards repeatedly define earthing (what 'whole house' protectors do) as essential to electronics protection. Meanwhile Bud also cites Martzloff while forgetting to quote what Martzloff recommends: High-current surges ... are best diverted at the service entrance of the premises. While such a protection is not mandated at present, trends indicate growing interest in this type of surge protection. Bud just forgets to mention that Martzloff recommends "service entrance" protection - also called a 'whole house' protector. One 'whole house' surge protector at about $1 per protected appliance that earths for protection. Exactly how all high reliability facilities did it even in the 1930s - because real protection was required. Read up top what Bud posted. Plug-in protector will not accomplish that. Only 'whole house' protection accomplishes that. Bud just forgot to mention that fact. But then who does he promote for? Bud would even hope you believe current technology protectors did not create these scary pictures: http://www.hanford.gov/rl/?page=556&parent=554 http://www.westwhitelandfire.com/Art...Protectors.pdf http://www.ddxg.net/old/surge_protectors.htm http://www.zerosurge.com/HTML/movs.html |
do I need a surge protector?
On Feb 26, 12:08 am, "w_tom" wrote:
On Feb 25, 3:19 am, "bud--" wrote: What happens to "connected to the same plug-in suppressor" electronics when a kid attaches his Xbox to the TV? Protection is completely compromised - as Bud's own citations note when discussing 'six ports'. "Six-ports" is in none of my citations. Six-ports is in a Martzloff paper where he talks about surge reference equalizers (aka multiport surge suppressors), which were new at the time of the paper. He said: "The surge reference equalizer combines the protective function for both system ports [power and signal] in the same enclosure. The device is plugged in the power receptacle near the equipment to be protected, with the communications system wires (telephone or data link) or the coaxial cable (TV) routed through the enclosure. A common, single grounding connection equalizes the voltages of the two paths that return the surge through the grounding connection of the 3-prong power line plug, as shown in Figure 4. "Such a solution is particularly attractive as an element of 'whole- house protection', a concept that has been recently introduced by some electric utilities." Martzloff recommends surge reference equalizers in the paper, just like he does in the NIST guide. But w_ can't understand how they work. A kid with an Xbox can. In one post, Bud recommends earthing so that 8000 volts does not damage a TV. In another, Bud claims "surge reference equalizer" does not require earthing. Which is it? w_ is forced to misrepresent information that conflictes with his beliefs.. What I have said, and what the IEEE guide says, is that plug- in surge suppressors work primarily by CLAMPING the voltage on all wires (power and signal) to the common ground at the suppressor. They do not work PRIMARILY by earthing. 8kV is part of the IEEE guide explanation of how plug-in suppressors work. Since it does not work primarily by earthing it violates w_'s religious beliefs and he is not able to understand the IEEE description. He hopes you will not notice this. No plug-in protectors manufacture claims to provide such protection in their numerical specifications. If they did, then they could be sued. This may be the stupidest thing w_ says. Specs are readily available, along with protection guarantees for many devices. Why does Bud intentionally distort what even the IEEE recommends in standards? Remember IEEE does not recommend in papers. IEEE recommends in standards. And IEEE standards repeatedly define earthing (what 'whole house' protectors do) as essential to electronics protection. Why does w_ refuse to acknowledge that the IEEE Emerald book, an IEEE standard, includes plug-in suppressors (surge reference equalizers) as an effective protection device? Why is w_ stupid enough to say the IEEE would publish a guide for the general public that is not consistent with IEEE standards? Bud just forgets to mention that Martzloff recommends "service entrance" protection - also called a 'whole house' protector. From the NIST guide, written by Martzloff, [who was the surge guru at the NIST]: "Q - Will a surge protector installed at the service entrance be sufficient for the whole house? A - There are two answers to than question: Yes for one-link appliances, No for two-link appliances [equipment connected to power AND phone or CATV or....]. Since most homes today have some kind of two-link appliances, the prudent answer to the question would be NO - but that does not mean that a surge protector installed at the service entrance is useless." But then who does he promote for? I agree with w_: "It is an old political trick. When facts cannot be challenged technically, then attack the messenger." My only interests in surge protectors are that I have two. Bud would even hope you believe current technology protectors did not create these scary pictures: Lacking technical arguments w_ tries scare tactics. http://www.hanford.gov/rl/?page=556&parent=554 http://www.westwhitelandfire.com/Art...Protectors.pdf http://www.ddxg.net/old/surge_protectors.htm http://www.zerosurge.com/HTML/movs.html For anyone with minimal reading skills the hanford link talks about "some older model" power strips and specifically references the revised UL standard, effective 1998, that requires a thermal disconnect as a fix for overheating MOVs. Overheating was fixed in the US in 1998. w_ can't understand his own links None of these links indicate the problem suppressors shown had UL labels. And none of these links say there is any problem with suppressors under the current UL standard. Or that plug-in suppressors shouldn't be used. The links do give info on how to use plug-in suppressors. And still no links that say plug-in suppressors are not effective - just w_'s ranting. But both the IEEE and NIST say plug-in suppressors are effective. As does Martzloff in a new source above. -- bud-- |
do I need a surge protector?
On Feb 25, 4:32 am, "Leonard Caillouet" wrote:
Joule ratings are not necessarily reliable indicators for comparison. The IEEE guide - linked to elsewhere - makes the same observation, saying there is no standard for how to make energy measurements, so measurements are not comparable. Let through voltage and current peak ratings are other ratings that should be considered. BTW, w_tom stated that most units start to clamp at 330volts, but actually, the better units these days have a max let through voltage of 330 volts. Sounds reasonable, but... François Martzloff was the surge guru at the NIST and wrote the NIST guide to surges linked in another post. From a Martzloff technical paper - pdf-page 20: http://www.eeel.nist.gov/817/pubs/sp...es/Enduser.pdf "The fact of the matter is that nowadays, most electronic appliances have an inherent immunity level of at least 600 V to 800 V, so that the clamping voltages of 330 V widely offered by TVSS manufacturers are really not necessary. Objective assessment of the situation leads to the conclusion that the 330 V clamping level, promoted by a few manufacturers, was encouraged by the promulgation of UL Std 1449, showing that voltage as the lowest in a series of possible clamping voltages for 120 V circuits. Thus was created the downward auction of "lower is better" notwithstanding the objections raised by several researchers [B8] and well-informed manufacturers. One of the consequences of this downward auction can be premature ageing of TVSS that are called upon to carry surge currents as the result of relatively low transient voltages that would not put equipment in jeopardy." Martzloff also wrote a guide for phone service reps for co-op power utilities. http://www.eeel.nist.gov/817/pubs/sp...shoot%20PQ.pdf This guide is considerably more technical than the IEEE guide, and includes a lot of information on surges caused by powerline switching Among his comments - pdf-page 20: "In fact, the major cause of TVSS failures is a temporary overvoltage, rather than an unusually large surge." At the risk of insulting anyone's intelligence, Martzloff said lower clamp voltages are not necessarily a good idea because they cause a suppressor to clamp surges that are not a risk to equipment, which may cause earlier suppressor failure than necessary. The suppressor also may try to clamp temporary overvoltage that would otherwise be ignored which will rapidly burn out MOVs, while the overvoltage continues. (That may provide protection for equipment connected to a plug-in suppressor if the protected equipment is connected across the MOVs and is disconnected when the MOVs are disconnected on failure. The protected equipment may also be connected so it is not disconnected - described in detail in the IEEE guide.) -- bud-- |
do I need a surge protector?
"bud--" wrote in message ps.com... On Feb 25, 4:32 am, "Leonard Caillouet" wrote: Joule ratings are not necessarily reliable indicators for comparison. The IEEE guide - linked to elsewhere - makes the same observation, saying there is no standard for how to make energy measurements, so measurements are not comparable. Let through voltage and current peak ratings are other ratings that should be considered. BTW, w_tom stated that most units start to clamp at 330volts, but actually, the better units these days have a max let through voltage of 330 volts. Sounds reasonable, but... François Martzloff was the surge guru at the NIST and wrote the NIST guide to surges linked in another post. From a Martzloff technical paper - pdf-page 20: http://www.eeel.nist.gov/817/pubs/sp...es/Enduser.pdf "The fact of the matter is that nowadays, most electronic appliances have an inherent immunity level of at least 600 V to 800 V, so that the clamping voltages of 330 V widely offered by TVSS manufacturers are really not necessary. Objective assessment of the situation leads to the conclusion that the 330 V clamping level, promoted by a few manufacturers, was encouraged by the promulgation of UL Std 1449, showing that voltage as the lowest in a series of possible clamping voltages for 120 V circuits. Thus was created the downward auction of "lower is better" notwithstanding the objections raised by several researchers [B8] and well-informed manufacturers. One of the consequences of this downward auction can be premature ageing of TVSS that are called upon to carry surge currents as the result of relatively low transient voltages that would not put equipment in jeopardy." Martzloff also wrote a guide for phone service reps for co-op power utilities. http://www.eeel.nist.gov/817/pubs/sp...shoot%20PQ.pdf This guide is considerably more technical than the IEEE guide, and includes a lot of information on surges caused by powerline switching Among his comments - pdf-page 20: "In fact, the major cause of TVSS failures is a temporary overvoltage, rather than an unusually large surge." At the risk of insulting anyone's intelligence, Martzloff said lower clamp voltages are not necessarily a good idea because they cause a suppressor to clamp surges that are not a risk to equipment, which may cause earlier suppressor failure than necessary. The suppressor also may try to clamp temporary overvoltage that would otherwise be ignored which will rapidly burn out MOVs, while the overvoltage continues. (That may provide protection for equipment connected to a plug-in suppressor if the protected equipment is connected across the MOVs and is disconnected when the MOVs are disconnected on failure. The protected equipment may also be connected so it is not disconnected - described in detail in the IEEE guide.) -- bud-- I would rather have it clamp to a lower voltage and be safer. Small surges that would fall between 330V and 600V are going to be tolerated by modern MOVs repeatedly. With the units that offer a lifetime warranty and a vendor that is quick to replace them, I'll take the risk of damaging the MOVs and protecting the equipment. You always know when an MOV is shot because they fail with a dead short, causing the breaker to open. Rather than buy cheaper units that use MOVs which are likely not as well made, I'll stick with the ones from companies that seem to make a reasonable trade-off between value and best protection. I don't necessarily disagree with your information, and thank you for keeping us informed on what is being published, but in the real world, people have to have something to go on. None of the ratings are a perfect representation of the best TVSS. I think you have to look at the whole picture and use common sense. That is where I came up with the two recommended units that I have posted previously and below. If you have any better suggestions, I would be very interested to see how you sort out what is available. Il kile the first because it is cheap and has more outlets and after taking them apart, I find that it has comparable protection to the Panamax for the a.c. and what I consider adequate protection on the signal lines. I like the second because of the similar protection, reputation of the company, the over/under voltage cutoff feature, and slightly better info, and perhaps clamping, on the signal line protection. To summarize, my suggetions for best value in surge protection a http://www.newegg.com/Product/Produc...82E16812120408 or http://www.panamax.com/products.cfm?...il&id=249&ly=v and verifying the integrity and correctness of the grounding on the a.c. service and ALL incoming signal lines. Additional whole house suppression is not a bad idea but one must note that most do not include protection for incoming signal lines nor do the have lifetime warranties like the system level units above. If anyone has a better recommendation, I am always shopping for the best values and searching for the most effective practices in the context of the market as it is applied to consumer electronics. And thanks, Bud, for debunking w_tom and his foolishness. Leonard -------------------------------------------------------------------------------- I am using the free version of SPAMfighter for private users. It has removed 940 spam emails to date. Paying users do not have this message in their emails. Try SPAMfighter for free now! |